> Need Help Guys, Design Idea help
richardv24
Posted: March 21, 2013 05:32 pm
Reply to this postQuote Post


Newbie
*

Group: Members+
Posts: 2
Member No.: 37,955
Joined: March 21, 2013




Hi Guys,

Ended up on this forum looking for help. Read through a few things and it seems really fun and interesting. Not sure if I am posting in the right section

Here is my situation.

I have projects where I get many motors (lets say anywhere from 8-100) hooked to a single power supply. The problem is when the motors all turn on at the same time, I get a huge in-rush current that trips the breakers. I was wondering if there would be some way using something like a PCB that would take the supply power and split it to each 460 volt motor but have each motor turn on within 1 second from each other.

So I need something so that all the motors turn on separately so there would be no HUGE in-rush current.

Thanks for any help.
PMEmail Poster
Top
kellys_eye
Posted: March 21, 2013 08:24 pm
Reply to this postQuote Post


Forum Addict ++
*******

Group: Spamminator Taskforce
Posts: 9,979
Member No.: 2,735
Joined: June 21, 2005




A properly designed PSU would cater for the inrush. What voltage/current rating are the motors?


--------------------
May contain nuts
PMEmail PosterYahoo
Top
richardv24
Posted: March 21, 2013 09:44 pm
Reply to this postQuote Post


Newbie
*

Group: Members+
Posts: 2
Member No.: 37,955
Joined: March 21, 2013




Thanks for responding.

The voltage is 480 and the inrush current is about 120 amps for a very short duration. I would appreciate being guided to some kind of an example that does something like this.

Thanks again
PMEmail Poster
Top
Sch3mat1c
Posted: March 22, 2013 12:14 am
Reply to this postQuote Post


Forum Addict ++
Group Icon

Group: Moderators
Posts: 18,142
Member No.: 73
Joined: July 24, 2002




Supply all the motors from contactors; sequence the contactors with time-delay relays.

Tim


--------------------
Answering questions is a tricky subject to practice. Not due to the difficulty of formulating or locating answers, but due to the human inability of asking the right questions; a skill that, were one to possess, would put them in the "answering" category.
PMEmail PosterUsers Website
Top
CWB
Posted: March 22, 2013 12:55 am
Reply to this postQuote Post


Forum Addict ++
*******

Group: Spamminator Taskforce
Posts: 19,511
Member No.: 15,154
Joined: May 15, 2008




"The voltage is 480 and the inrush current is about 120 amps for a very short duration"

is that total current or for each motor ?

yep ... a sequenced contactor system is the best bet .
if you want to save a lot of headaches in design there are industrial time delay controllers/contactors that can send a trigger to the next contactor unit down the line .
the time delay before triggering the next unit is essential ... each motor has to come up to speed in order for the current draw to drop .

you mentioned 8 to 100 motors ... be prepared to thin down your wallet .


--------------------