Posted: March 21, 2013 05:32 pm
|
|
Newbie ![]() Group: Members+ Posts: 2 Member No.: 37,955 Joined: March 21, 2013 |
Hi Guys,
Ended up on this forum looking for help. Read through a few things and it seems really fun and interesting. Not sure if I am posting in the right section Here is my situation. I have projects where I get many motors (lets say anywhere from 8-100) hooked to a single power supply. The problem is when the motors all turn on at the same time, I get a huge in-rush current that trips the breakers. I was wondering if there would be some way using something like a PCB that would take the supply power and split it to each 460 volt motor but have each motor turn on within 1 second from each other. So I need something so that all the motors turn on separately so there would be no HUGE in-rush current. Thanks for any help. |
| kellys_eye |
Posted: March 21, 2013 08:24 pm
|
![]() Forum Addict ++ ![]() ![]() ![]() ![]() ![]() ![]() ![]() Group: Spamminator Taskforce Posts: 9,979 Member No.: 2,735 Joined: June 21, 2005 |
A properly designed PSU would cater for the inrush. What voltage/current rating are the motors?
-------------------- May contain nuts
|
| richardv24 |
Posted: March 21, 2013 09:44 pm
|
|
Newbie ![]() Group: Members+ Posts: 2 Member No.: 37,955 Joined: March 21, 2013 |
Thanks for responding.
The voltage is 480 and the inrush current is about 120 amps for a very short duration. I would appreciate being guided to some kind of an example that does something like this. Thanks again |
| Sch3mat1c |
Posted: March 22, 2013 12:14 am
|
![]() Forum Addict ++ Group: Moderators Posts: 18,142 Member No.: 73 Joined: July 24, 2002 |
Supply all the motors from contactors; sequence the contactors with time-delay relays.
Tim -------------------- Answering questions is a tricky subject to practice. Not due to the difficulty of formulating or locating answers, but due to the human inability of asking the right questions; a skill that, were one to possess, would put them in the "answering" category.
|
| CWB |
Posted: March 22, 2013 12:55 am
|
![]() Forum Addict ++ ![]() ![]() ![]() ![]() ![]() ![]() ![]() Group: Spamminator Taskforce Posts: 19,511 Member No.: 15,154 Joined: May 15, 2008 |
"The voltage is 480 and the inrush current is about 120 amps for a very short duration"
is that total current or for each motor ? yep ... a sequenced contactor system is the best bet . if you want to save a lot of headaches in design there are industrial time delay controllers/contactors that can send a trigger to the next contactor unit down the line . the time delay before triggering the next unit is essential ... each motor has to come up to speed in order for the current draw to drop . you mentioned 8 to 100 motors ... be prepared to thin down your wallet . -------------------- "Know how to solve every problem that has been solved"
R. Feynman '88 |
![]() |
![]() ![]() ![]() |